It's Really an industrial plant and definitely not where anyone but maintenance would need it. and He is saying because concrete in "conductive" and you might have to lay down to work on it so there's a code saying you cant do it. P.S. I know that sounds ridiculous but this is the stuff I deal with on a regular basis. I Just want to bring these questions to the forum to make sure im not overlooking any codes. I appreciate your response!! ThanksThis is definitely not an NEC requirement. Commercial installations often need to comply with ADA requirements but the NEC is silent on the height.
Welcome to the Forum.![]()
As a general rule for safety reasons you are normally not supposed to work on it while it is energized so laying on the concrete to work on it doesn't really introduce additional electrical hazards, might increase your chances of being run over by a forklift or something though.It's Really an industrial plant and definitely not where anyone but maintenance would need it. and He is saying because concrete in "conductive" and you might have to lay down to work on it so there's a code saying you cant do it. P.S. I know that sounds ridiculous but this is the stuff I deal with on a regular basis. I Just want to bring these questions to the forum to make sure im not overlooking any codes. I appreciate your response!! Thanks
No nothing like that.Being an industrial setting, is this a hazardous location? Explosive gases, fibers or dust may be present?
Correct NEC doesn't require a receptacle at all.The only location the NEC requires a receptacle is for electrical service rooms and for HVAC. Other than that, no receptacles are required. And I appreciate your attitude, in the electrical field we get a lot of "this is required" but no actual language says that. Mike Holt would say "is this what you think or what you know"
If you electrician is concerned about the concrete floor, a GFCI is the safe and low cost solution to that.
Thats the only thing other than ADA that would have a height requirement.No nothing like that.
18" is still not very accessible behind a sheet of plywood leaned against the wall.In my shop I put the receptacles at 4 ft 6" so they are above a sheet of plywood leaned against the wall. Seems like ADA is 18".
Kind of leaves the door for interpretation wide open doesn't it? Maybe useful for receptacles intended for a specific appliance but still leaves you wondering for most anything else.The Code of Federal Regulations 28 Part 36 (American Disabilities Act) in Section 4.27.3 states that electrical and communications system receptacles on walls shall be mounted no less than 15" above floor. However, the exception indicates that this does not apply to receptacles not intended for use by building occupants. The maximum height for receptacles and/or switches is between 48 and 54 inches, depending on the conditions, see Section 4.2.5 and 4.2.6 of the ADA.