Ok, I can see that part of what was done is legal. Since I didn't describe it too well...and yes I need to learn terminology. We have 2 control panels that are fed from a 460 volt 30 amp circuit. I call it a 30A because the feeders come from a service panel with a 30A breaker. At the top lugs of panel #1 disconnect switch, 3 wires are tapped off and run to panel #2 disconnect. The run to panel 2 is about 20 feet.
What I left out before is the real reason I called it half assed work. In each of the 2 panels there are no fuses, no circuit breakers inline with the feeds off the disconnect switches. According to article 240.21 the taps must terminate in a breaker or fuses. So, this is a code violation. Thanks for pointing me to where taps are described.
The same outfit built a lot of our panels. Typically they have no fuses or breakers other than the overloads in the motor starters and contactors. The control transformers usually come with fuse blocks so those are protected. So, these panels are a problem and one of the reasons I was hired. We will be slowly replacing a lot of these.
Once again thanks for the pointers and good advice. It is a huge help and is exactly what I was hoping for on this forum. And I appreciate you guys not being too hard on me
.