electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
I think I understand demand charges and demand billing. I also just read the explanation from national grid. Take a look at this bill. I am not following why the demand charges are so high. Where is the "billed demand" of 105 KW coming from? Does something seem wrong?
View attachment 19403
Do you even have 205 kVA service to this meter, or anything behind it that's capable of consuming 205 kW? It might be a metering or billing error.Your electric company is a bastard... just did a brief bit of research, and apparently, some month in the last 11 months you had a demand of 210kw. ...
I might add that I'm not understanding why the bill says demand as 9.6 KW but the billed demand is 105 KW. Must be something I'm not understanding here.
Ok that explains it. Thanks guys. This is a 1000 amp 120/208 service. As you can see from the kwh usage, there is very little load currently, however they did have some growers in there a year ago so that 210 kw demand is reasonable. Wow, demand is a bitch....
Yep, I think you are correct. I was not thinking of a ratchet clause but that would explain it.Thats what I referenced the ratchet clause for... doesn't matter what his actual demand was, his minimum demand charge is half of his highest demand charge from the previous 11 months...
Yep, I think you are correct. I was not thinking of a ratchet clause but that would explain it.
I know many have a real issue with power rates but I see the business case for justifying demand and time of use rates. After all it cost the POCO to supply demand. For me though, I draw the line at tiered rates which is sweeping the nation that I see as nothing but pure socialism. I see no justification for this from a cost of providing service to the POCO.
And apparently they are gouging a new user based on what the previous user did - though they may not have the same kind of operation.I can appreciate that a POCO needs to plan it's demand profile and cover it's costs when you blow the curve, but this is excessive. It should take into account the delta between your base load and your peak. If you are a steady customer, they can build you into the base load plan. Only if you swing wildly should you pay accordingly. Again, the plan in this thread just gouges the customer.
Seventy cents a kilowatt hour?
That's if you divide the total bill by the actual kWh.
It actually works out to an energy charge just over $.08, misc. delivery charges totaling maybe $.02, and $1000 of load-independent fake demand charge.
It costs money to build & maintain generation, transmission & distribution, regardless of how much energy they deliver.
Demand charges are one way to recoup those costs.
This is how you make renewables economically viable.
I don't know, I think it is tough to use solar to lower demand penalties - at least here in the northeast, maybe a much sunnier place it would help reliably. Here, you will certainly get lucky now and then, but all it takes is 1 15 minute interval and you are screwed.