Help! Boss's Ratty Work

Status
Not open for further replies.

big john

Senior Member
Location
Portland, ME
A buddy of mine referred me to one of these handy-man types for some side-work. The handy-man has some decent all around knowledge but his only formal training is as a boiler tech. He seems to have some basic electrical knowledge (can wire 4-way switches; knows that the EGC isn't just a pesky "extra wire") but he's cheap, and that cheapness leads to some really shoddy work, which puts me in a place I don't want to be in.

Example:</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Splicing a circuit in an old ungrounded octagonal box. I went to put in the ground screw, but for some reason it wouldn't start in the hole. I asked the guy if he had a tapping tool so I could re-thread the hole and his reply is: "Just put it under a pan-head [wood screw]."</font>
<font size="2" face="Verdana, Helvetica, sans-serif"> </font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">I need an anti-short bushing for some AC and we're fresh out.
    "I don't want to stop the whole job for one bushing, use electrical tape!"</font>
<font size="2" face="Verdana, Helvetica, sans-serif">:mad:

I feel like I do better electrical work than this handy-man any day of the week, so I'd much rather do it myself. But, doing it myself means that I'm might be forced to do poorer-than-average work because I don't have the tools/materials to do it right. :mad:

I haven't seen him do anything that is drastically unsafe, yet, but I figure it's only a matter of time... What can I do? :confused:

HELP!

-John

P.S.: I'm going to replace the old octagonal with a 1900 box so I can properly ground the thing.
And, by god, I searched around until I found an anti-short bushing to use instead of tape.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Help! Boss's Ratty Work

Boss or no boss, YOU are the electrician and he is not! Have a talk with him and set things straight. If he won't allow you to do your work safely and properly as you know how, do yourself a favor and quit. The poor workmanship will be a reflection on you and if anything serious should happen you certainly don't want to be involved with the jerk.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Help! Boss's Ratty Work

Oh, I don't understand what you mean by But, doing it myself means that I'm might be forced to do poorer-than-average work because I don't have the tools/materials to do it right.

Are you saying that if you did work on your own you don't have your own tools or can't get materials?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Help! Boss's Ratty Work

Guys John is an Electrical Apprentice.

He does not yet have his license.

That said I would be glad to have him work with me, as he has something much more important IMO.

Pride in his work :)

John IMO you have two choices, do it his way or move on.

Only you know what you can afford to do.

Which is worse to you the anguish of doing poor work or the loss of revenue.

Good luck whatever your choice and do not let this guy corrupt your good attitude. :)

[ October 26, 2003, 03:53 PM: Message edited by: iwire ]
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Help! Boss's Ratty Work

John just so you know you are not alone, I got fired and left in the city 20-25 miles from home because I would not do things I knew then as an apprentice where wrong. :)

Bob
 

drg

Senior Member
Re: Help! Boss's Ratty Work

John,

I am rotated between several work crews as a beginner electrican and boy do I ever have to adjust to doing things different,

Learning how to work with a "schlock" is probaly the hardest thing one can do.

If it was a side job "just keep doing what you need to do", and if he fires you so what !!

Johnhatesworkingwithschlocks

I did not edit anything , I just wanted to see how it works.
Johnnowknowshowtoedit

[ October 26, 2003, 06:26 PM: Message edited by: drg ]
 
G

Guest

Guest
Re: Help! Boss's Ratty Work

Ask him if he will put you in charge of quality control. When he tells you to do something you know is not code is he at all open minded? If you told him the sheet metal screw is not code would he listen? Let him know that you are willing to look things up in the NEC and help him improve his game. Tell him that if you're not sure about something you will find the answer so it can be done right. He may be uninformed, but willing to accommodate your knowledge of the code. Ask him point blank before you burn the bridge. You might be able to make yourself indispensable to him by getting yourself in charge of quality control and in charge of making sure things are NEC compliant. You might hint at the liability issue too. You can help save him from a lawsuit resulting from any damages incurred from improper work. It's worth a shot. Hit him right between the eyes and see how he reacts. Good luck!
 

drg

Senior Member
Re: Help! Boss's Ratty Work

Wayne, if you read over what John originally posted about the guy, with the green grounding screw and use of electrical tape you already should have figured out what this guys whole game is.

The guy is a handyman and not a tradesman.

Blathering on with this handyman would be not worthwhile in my opinion and probaly just cause a attitude with the handyfellow.

Johnunderstandsjohnssituation
 
G

Guest

Guest
Re: Help! Boss's Ratty Work

John,
Points well taken. I agree, it may be a lost cause, but I would give it one final bump before John burns the bridge with handyboss. John should stand firm on doing things to code. I'm just thinking there may be a chance that handyboss doesn't know about the NEC code barring the use of sheet metal screws for ground keepers. He probably knows better about the red anti-short bushing.

Don't lump handyboss on the slag heap of hopeless handymen yet. There may be hope for him. He hired John. That speaks well in itself :)

Also, if he's doing jobs under a certain dollar amount there may be no licensing requirement in his state.

The violations mentioned are not terribly egrigious, and hopefully he is openminded about improving his game. John can be the craftsman & quality control point man. That's all.

../Wayne C.

[ October 26, 2003, 09:33 PM: Message edited by: awwt ]
 

hurk27

Senior Member
Re: Help! Boss's Ratty Work

If you have a printer print this artical and tell your boss that you have to go by the code or this is what could happen!

000098_G.jpg


Sorry joe but it was the only good example I could think of.
 

big john

Senior Member
Location
Portland, ME
Re: Help! Boss's Ratty Work

Thank you guys for your replies, I think I'm gonna try the education approach, see if I can't change his ways. If not, then I guess I'll walk. I'm just frustrated. We're working in a house that's already full of ridiculously backwards work from installations past:

</font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Two 10x10x4 inch J-boxes that hold upwards of forty circuits, only about five of which are identified.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">A 12 by 12 foot kitchen with sixteen GFCI duplex receptacles all on dedicated circuits.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">Abandon cable and J-boxes everywhere.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
  • <font size="2" face="Verdana, Helvetica, sans-serif">An AFCI breaker with three bedroom circuits on it [read as: Three conductors under one screw.]</font>
<font size="2" face="Verdana, Helvetica, sans-serif">And on top of that I have to deal with a guy who's new installation practices involve gluing 1900 boxes to masonry walls because he doesn't want to waste the plastic anchors.

I haven't walked yet because I have the skills to make a lot of this nonsense right and ensure that new stuff is done properly. I feel a responsibility to see that the work is done correctly, especially since I know that when I leave, all bets are off.

Ugh. Thanks again, gentlemen.

-John

[ October 26, 2003, 10:06 PM: Message edited by: big john ]
 

drg

Senior Member
Re: Help! Boss's Ratty Work

That is a good impact message , but some folk would still try to rationalize their own reasons for short cutting and disregard this .
While this message will make any normal person think, realize that there are a lot of people out there that are not normal.
If you are dealing with the latter of the 2 you better be able to make desicions for yourself, and if that means getting fired or walking off a job so be it, you probaly fighting the whole thing by being there in the first place.

Johnagreeswiththemessagepoint
I wrote this in reply to the electrican get 5 years sentence post!!

[ October 26, 2003, 10:29 PM: Message edited by: drg ]
 

brian john

Senior Member
Location
Leesburg, VA
Re: Help! Boss's Ratty Work

Big John:

If you'd like to work for a quality company, contact me by private email and I can put you in touch with several electrical contractors that would appreciate your concern and williness.


Brian John
 

rickcham

Member
Re: Help! Boss's Ratty Work

Big John

I think you now see the difference between the "handyman" and a true "craftsman" you keep your mind set to do things corectly and you will go far in the trades!!
Wish you the best of luck with this one.

Rick
 

larryl

Senior Member
Location
wrentham ma.
Re: Help! Boss's Ratty Work

hey big john
congrats on your work ethic!!!this guy isn't gonna change,especially for you,its his nature not to care,
i'm a seasoned 20 year man(on my own in the south boston erea) and its great to here from a guy that cares,,
you've probably dumped this bum already,by the time you read this,,and i'm sure you feel better about yourself for doing so,
sounds like your a good guy with alot of potential,,
GET ANOTHER JOB,,and stay in the field,,your gonna do great .the industry needs people like you!!look in the paper or go on line,,
put your name up at the your supply house,, letting people know your looking for work,,believe me ,,you're gonna work for alot of people throughout your carrier,,
GOOD LUCK,,
 

larryl

Senior Member
Location
wrentham ma.
Re: Help! Boss's Ratty Work

hey big john
congrats on your work ethic!!!this guy isn't gonna change,especially for you,its his nature not to care,
i'm a seasoned 20 year man(on my own in the south boston erea) and its great to here from a guy that cares,,
you've probably dumped this bum already,by the time you read this,,and i'm sure you feel better about yourself for doing so,
sounds like your a good guy with alot of potential,,
GET ANOTHER JOB,,and stay in the field,,your gonna do great .the industry needs people like you!!look in the paper or go on line,,
put your name up at the your supply house,, letting people know your looking for work,,believe me ,,you're gonna work for alot of people throughout your carrier,,
GOOD LUCK,,
 

pamster00

New member
Re: Help! Boss's Ratty Work

I've got some questions.

First the background. I've got a UPS to install in a server room at work. It needs a 20A receptacle and except for one 30A singleton with a larger UPS plugged into it, everything is 15A dual receptacles. I showed the facility manager what I needed and asked for a 20A circuit to be installed. He stepped out of the room briefly, then returned and said that several orange 15A receptacles were on 20A circuits and he'd have his guy change some of the receptacles.

My first question is would a responsible operator have installed 20A service without placing 20A receptacles?

I later returned to the room and found that two of the 15A receptacles had been changed for 20A ones. Each of the 20A receptacles shares a quad JBox with one of the original 15A ones. I do not know what wiring is actually entering the JBoxes.

When I plugged in the UPS and turned it on, I heard a loud click from somewhere. The device's on-battery power alarm did not sound, however, so I know the circuit breaker serving the receptacle did not trip off. I have not added any loads to the UPS yet.

I have reservations about this installation. What else can I look at?
 