Re: Help! Boss's Ratty Work

A general-purpose branch receptacle ciruit rated 20A can have 15 or 20 A receptacles.
See table 210.21(B)(2)
For a 20A branch circuit the maximum load is 16 amperes.

[ December 09, 2003, 02:55 PM: Message edited by: tom baker ]
 

maylo1st

Member
Location
Pennsylvania
Re: Help! Boss's Ratty Work

I know the feeling but you don't have to work for this guy. get out while the getting is good. Some people just don't know or worry about the codes or peoples safety.
 