i wanted to verify the answer on this question.

the question is...
service entrance conductors may be installed in
a) LFNC
b) 2.0 m of FMC
c) NM-B cable
d) 2.5m of LFMC

i believe the answer is a based on 230.43 (16), but im not sure :-?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
rm1212 said:
i wanted to verify the answer on this question.

the question is...
service entrance conductors may be installed in
a) LFNC
b) 2.0 m of FMC
c) NM-B cable
d) 2.5m of LFMC

i believe the answer is a based on 230.43 (16), but im not sure :-?
Are you not sure because of the 2.5m of LFMC or the abbreviations. Anyway you got it right-- service conductors can be installed in liquidtight flex. nonmetallic conduit -- it doesn't give a length. (a)
 

rm1212

Member
thank you for the response i wanted to make sure i was not missing something. i would hate to blow it by one or two answers.:)
 

davizaud

Member
Service entrance

Service entrance

Thanks again, I forgot about this article 240.43. I was searching SE cable like an idiot. as far as FMC you are right 1.8 meters is all we get.
 