R rm1212 Member Feb 18, 2007 #1 i wanted to verify the answer on this question. the question is... service entrance conductors may be installed in a) LFNC b) 2.0 m of FMC c) NM-B cable d) 2.5m of LFMC i believe the answer is a based on 230.43 (16), but im not sure :-?
i wanted to verify the answer on this question. the question is... service entrance conductors may be installed in a) LFNC b) 2.0 m of FMC c) NM-B cable d) 2.5m of LFMC i believe the answer is a based on 230.43 (16), but im not sure :-?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Feb 18, 2007 #2 rm1212 said: i wanted to verify the answer on this question. the question is... service entrance conductors may be installed in a) LFNC b) 2.0 m of FMC c) NM-B cable d) 2.5m of LFMC i believe the answer is a based on 230.43 (16), but im not sure :-? Click to expand... Are you not sure because of the 2.5m of LFMC or the abbreviations. Anyway you got it right-- service conductors can be installed in liquidtight flex. nonmetallic conduit -- it doesn't give a length. (a)
rm1212 said: i wanted to verify the answer on this question. the question is... service entrance conductors may be installed in a) LFNC b) 2.0 m of FMC c) NM-B cable d) 2.5m of LFMC i believe the answer is a based on 230.43 (16), but im not sure :-? Click to expand... Are you not sure because of the 2.5m of LFMC or the abbreviations. Anyway you got it right-- service conductors can be installed in liquidtight flex. nonmetallic conduit -- it doesn't give a length. (a)
R rm1212 Member Feb 18, 2007 #3 thank you for the response i wanted to make sure i was not missing something. i would hate to blow it by one or two answers.
thank you for the response i wanted to make sure i was not missing something. i would hate to blow it by one or two answers.
D davizaud Member Feb 18, 2007 #4 Service entrance Service entrance Thanks again, I forgot about this article 240.43. I was searching SE cable like an idiot. as far as FMC you are right 1.8 meters is all we get.
Service entrance Service entrance Thanks again, I forgot about this article 240.43. I was searching SE cable like an idiot. as far as FMC you are right 1.8 meters is all we get.