Just brushing up on my calcs. I saw this 500 kw 208/480 volt 3 phase transformer being fed off a 800 amp breaker.
I come up with 500,000/(1.73 X 480)=602.12 amps
602.12 amps per phase right??
The conductors appeared to be ran in parrallel about 4 ft long each (could only see the pipe not the conductors) There were 3 conduit runs(if i recall correctly) from the transformer to the 800 amp. I read table 450.3(B) it looks like you can go as high as 125% of the rating of the transformer for primary protection. 1.25 X 602.12=752.65 . According to 240.6 they dont make a 752 amp breaker so you can go to 800 amps on this, i also read the note #1 on table 450.3(B)
I dont have much experience on some of the transformers. so in each conduit
I assume are 3 4/0 cables (4/0 good at 230 amps table 310.16) and maybe one conduit has a 1/0 ground in one of them table 250.122 (800 amp overcurrent device) 3 X 230 amps= 690 amps.
But would this 800amp also serve as the ocpd for the primary conductors feeding the transformer?? I know the 800 amp can serve as the ocpd for the transformer itself but what about the conductors?? Do they not need overcurrent protection?? then again maybe its 250 mcm in this run thats parrelled.
How would an install like this normally be done??
I come up with 500,000/(1.73 X 480)=602.12 amps
602.12 amps per phase right??
The conductors appeared to be ran in parrallel about 4 ft long each (could only see the pipe not the conductors) There were 3 conduit runs(if i recall correctly) from the transformer to the 800 amp. I read table 450.3(B) it looks like you can go as high as 125% of the rating of the transformer for primary protection. 1.25 X 602.12=752.65 . According to 240.6 they dont make a 752 amp breaker so you can go to 800 amps on this, i also read the note #1 on table 450.3(B)
I dont have much experience on some of the transformers. so in each conduit
I assume are 3 4/0 cables (4/0 good at 230 amps table 310.16) and maybe one conduit has a 1/0 ground in one of them table 250.122 (800 amp overcurrent device) 3 X 230 amps= 690 amps.
But would this 800amp also serve as the ocpd for the primary conductors feeding the transformer?? I know the 800 amp can serve as the ocpd for the transformer itself but what about the conductors?? Do they not need overcurrent protection?? then again maybe its 250 mcm in this run thats parrelled.
How would an install like this normally be done??