I got a call today from a friend that just installed a large service at a commercial building. Seems he just got red flagged for the size of his equipment-bonding jumper for his parallel service conduits. He ran one wire through all the ground bushings on the service conduits.
What he did was take the circ mils of the largest phase conductor in each conduit, add together, took that number and applied it to table 250.66. His circ mils were over 1100. He then took the wording of the table to say, anything over 1100 shall be a 3/0 copper. So he bonded with a 3/0. The inspector told him no and made him multiply the largest phase conductor of each set by 12.5 from 250.28 D. His circ mils where over 1100 for table 250.66. So he went to chapter 9, table 8.
Here are the calcs.
4 rigid conduits.
3-350 phase conductors each conduit.
Each phase, 4 ? 350?s = 1400 circ mils each phase.
Electrician said, over 1100, just use a 3/0
Inspector, multiply circ mils by 12.5 and go to ch. 9 table 8.
1400 circ mils x 12.5 =175,000. 3/0 = 167,800 table 8
Have to use a 4/0. 211,600 table 8
After looking at the code fairly close, it would appear to me that they were both in error. Wouldn?t the rigid conduits be equipment? From what I can tell, they would fall under 250.92 A and 250.102C. It seems to me in my thinking. that you should run a bonding wire to each service conduit and size each bonding jumper to the total circ mils of the phase conductors in that conduit.
3 ? 350?s each conduit, phase wires =1050 circ mils.
Bond each conduit with a 2/0 copper wire.
However, if all the parallel conductors where in the same conduit, you would then take the total CM of all the wires of the same phase, add and then, multiply by 12.5% and get your bonding jumper from table 250.66.
Couple of questions.
I understand that on some parallel installations, we have to go to table 8 of chapter 9 just to find the total circ mills of a conductor. But where does it direct us in the code to use chapter 9 table 8 for actually sizing the bonding wire after a total circ mils has been found? Kind of weird that table 250.66 just says the term over 1100, use a 3/0
Also, What is the size of the grounding electrode conductor?
Again, table 250.66 Note 1.
Add all phase conductors of one phase together and go to table. If this were true, our example would be 1400 cm.
Do we use a 3/0 or do we go to a 4/0?
And the big question, Is the feeder conduits considered equipment in relation to bonding/grounding? I sure think so.
And if so, are we required to run a separate bonding wire to each one? If so, my service equipment won't look near as pretty and I have been doing it wrong for awhile!
Thanks, really interested to get the correct answer
What he did was take the circ mils of the largest phase conductor in each conduit, add together, took that number and applied it to table 250.66. His circ mils were over 1100. He then took the wording of the table to say, anything over 1100 shall be a 3/0 copper. So he bonded with a 3/0. The inspector told him no and made him multiply the largest phase conductor of each set by 12.5 from 250.28 D. His circ mils where over 1100 for table 250.66. So he went to chapter 9, table 8.
Here are the calcs.
4 rigid conduits.
3-350 phase conductors each conduit.
Each phase, 4 ? 350?s = 1400 circ mils each phase.
Electrician said, over 1100, just use a 3/0
Inspector, multiply circ mils by 12.5 and go to ch. 9 table 8.
1400 circ mils x 12.5 =175,000. 3/0 = 167,800 table 8
Have to use a 4/0. 211,600 table 8
After looking at the code fairly close, it would appear to me that they were both in error. Wouldn?t the rigid conduits be equipment? From what I can tell, they would fall under 250.92 A and 250.102C. It seems to me in my thinking. that you should run a bonding wire to each service conduit and size each bonding jumper to the total circ mils of the phase conductors in that conduit.
3 ? 350?s each conduit, phase wires =1050 circ mils.
Bond each conduit with a 2/0 copper wire.
However, if all the parallel conductors where in the same conduit, you would then take the total CM of all the wires of the same phase, add and then, multiply by 12.5% and get your bonding jumper from table 250.66.
Couple of questions.
I understand that on some parallel installations, we have to go to table 8 of chapter 9 just to find the total circ mills of a conductor. But where does it direct us in the code to use chapter 9 table 8 for actually sizing the bonding wire after a total circ mils has been found? Kind of weird that table 250.66 just says the term over 1100, use a 3/0
Also, What is the size of the grounding electrode conductor?
Again, table 250.66 Note 1.
Add all phase conductors of one phase together and go to table. If this were true, our example would be 1400 cm.
Do we use a 3/0 or do we go to a 4/0?
And the big question, Is the feeder conduits considered equipment in relation to bonding/grounding? I sure think so.
And if so, are we required to run a separate bonding wire to each one? If so, my service equipment won't look near as pretty and I have been doing it wrong for awhile!
Thanks, really interested to get the correct answer