Adamjamma
Senior Member
- Location
- Jamaica and london
Now, based upon the transition from the 200 amp main disconnect to the 100 amps in the pedestal, I would now put a breaker in the disconnect, to protect the 100 amp wires... but if the wires were capable of at least the original 200 amps all the way to the mobile home panel, then I do not see the need for the breaker in the pedestal when a 200 amp simple disconnect is capable of the job... but it may be cheaper to source the breaker switch than the simple DP switch at this time.