What kinds of load are you running? How much single phase L-N, single phase L-L and 3 phase? As others have asked are you the only customer on the transformer? I have 'fixed' voltage issues by having the POCO convert open delta to just a regular delta by adding another bank. In another recent thread we were discussing the effects of B-C connected L-L single phase loads on open delta system capacity.
we are the only customer on the transformers.. they are right outside the building on a pad.
I can't confirm wiring as they're pad mount and obviously we're not gonna mess with the power company's gear.
Service: 400amp from power company
Voltage inbalance exists on the rails BEFORE the panels, and even exists when the entire building is disconnected.
the more that I learn about open delta, this seems correct tho?
as far as major loads:
qty 3 - 3 phase motor loads (5hp)
qty 2 printing presses which use 3phase frequency drives and servo amplifiers (servo amplifiers are what are faulting out from high voltage). Manufacturer says open delta is no problem with these as long as the voltages after the buck boost transformers are less than 232v. Breakered at 40a each
qty 2 intermittent 'flash cure dryers' - 3phase 11kw heater load when first warming up, then cycling for a few seconds at a time.
very little L-L single phase... nearly all the other equipment is L-N 120v connections
I've confirmed there's no High-Leg to Neutral single breakers installed.
I'd have to clamp the feeds to get exact amperages, I haven't done that in a long time, but power company said that they saw nothing for concern when they were looking at the amount of current coming into the building.
Again, the head scratcher thing here is that everything has been fine since 2019 when we moved in... this just started a month ago... so almost nearly has to be the power company.
Yesterday after the lineman tagged out the caps things seemed better...
Time will tell