Articles 430.52 and 430.53 are for branch circuits. But you have to understand that prior to sizing the OCPD for feeder.
Article 430.62 says that the rating of a motor feeder short-circuit ground-fault protective device is determined by adding the rating of the largest branch-circuit short-circuit ground-fault protective device for any motor supplied by the feeder to the sum of the full-load currents of all of the other motors.
So the largest OCPD in your case is 65AX2.5=170.1A, the standard next low rating is 150A, you mentioned each motor has their own fuses. You can use the actual fuse rating as the largest OCPD. Then add the sum of the full-load currents of all of the other motors that is 7.6A. That sum is 157.6A and the standard breaker rating is 150A. So the OCPD for the feeder will be 150A breaker in your case.
Articles 430.52 and 430.53 are for branch circuits. But you have to understand that prior to sizing the OCPD for feeder.
Article 430.62 says that the rating of a motor feeder short-circuit ground-fault protective device is determined by adding the rating of the largest branch-circuit short-circuit ground-fault protective device for any motor supplied by the feeder to the sum of the full-load currents of all of the other motors.
So the largest OCPD in your case is 65AX2.5=170.1A, the standard next low rating is 150A, you mentioned each motor has their own fuses. You can use the actual fuse rating as the largest OCPD. Then add the sum of the full-load currents of all of the other motors that is 7.6A. That sum is 157.6A and the standard breaker rating is 150A. So the OCPD for the feeder will be 150A breaker in your case.