meternerd
Senior Member
- Location
- Athol, ID
- Occupation
- retired water & electric utility electrician, meter/relay tech
One thing to keep in mind....many, single phase conditions are on the primary side of the transformer. On a typical 3 PH Wye or Delta system, a motor can continue to operate both starting and running with one primary phase missing. This is because most pad-mount transformer use common core windings, where the core is shaped like double-H and the induced voltage in the missing phase will be enough to keep the motor operating. But...voltages will be unbalanced and motor overheating will probably occur. I've seen quite a few instances where a KWH meter showed odd phase voltages which turned out to be blown primary fuses, but the pump station continued to run. That's why we install phase monitors that trip on phase current or voltage imbalance. Overloads don't always provide protection.