I'm spec'ing three feeds to be run out of an existing MCC, each feed will be fed seperately from its own bucket containing a 3phase breaker.
1. I need 1 feed from the MCC for a 15KVA, 1phase lighting transformer (31.2A primary @480v)
2. 1 feed from the MCC to supply 150A/480v/3ph to supply some general motor loads fed from existing combination starters. The total motor load is much less than the feed size (around 50A), but feed will be available for future use.
3. 1 feed from the MCC to supply 100A/480v/3ph to supply several fans w/ existing fusible disconnects. Total fan load is around 50a maximum.
So, my questions is twofold:
1. I understand the conductor size to be calculated by multiplying the total load by 1.25, so to provide a 100A feed, my wire size
would have to be good for 125A, or #2AWG@ 90C per table 310.16, correct?
2. What is the correct way (by code) to size the breaker protecting the feeder?
Thanks!!