winnie
- Springfield, MA, USA
- Electric motor research
This 3 phase 240 v motor runs at 12 amps and T 430.250 shows 15.2 amps
So if the motor draws 12 amps on 3 phase then what would the draw be on the feeder which is single phase. Is this what @Dzboyce is talking about. The feeder would be drawing 28 amps based on 5 hp single phase motor?????
The VFD is a pretty efficient power converter, likely better than 95%. So the current into the VFD will pretty much be whatever is necessary to supply the true power consumption of the motor. The VFD supplies any reactive power needed by the motor.
Basically the input current to the VFD is almost completely disconnected from the current being consumed by the motor. Think 'transformer' where the primary and secondary current can be radically different, but with a VFD the transformation ratio can change.
If you are asking what the NEC requires, the circuit to the VFD must be rated based on the input capacity of the VFD, not any sort of calculation based on the connected motor.
Jon