0141023-0729 EDT
5 S Electric:
I don't believe you are using a logical troubleshooting procedure. Guessing, replacing, and try are not an effecdtive troubleshoot approach if you can get quantitative information at various points in the system. Your system does not prevent you from making measurements at various intermediate points.
To troubleshoot a system you need to know how the system works. Then you need to make measurements at different parts of the system, and correlate the data with what would make sense for the probed poiints.
You need voltage information and so far I don't see any voltage data. Fundamentally a simple UPS makes use of input voltage to determine its action.
Ask yourself how a UPS works, there are various kinds. Search the Internet for a discussion.
In Google enter the search string:
how does a ups work
Some results are:
http://computer.howstuffworks.com/question28.htm
http://en.wikipedia.org/wiki/Uninterruptible_power_supply
and others.
In posts #2 and #3 I provided you some starting points for troubleshooting.
Why do UPSs randomly change state? If they are in good working condition the reason is the UPS has detected an input voltage that is outside its threshold limits. Not all UPSs of the same model have exactly (precisely) the same voltage thresholds, nor is a threshold likely to be precisely stable over a long time.
It is unlikely you have any UPSs that can run from battery for 40 minutes after a dip in voltage unless the input voltage rises to a level that can keep the battery charged, but not sufficiently high to reconnect the load to the input power source.
.
5 S Electric:
I don't believe you are using a logical troubleshooting procedure. Guessing, replacing, and try are not an effecdtive troubleshoot approach if you can get quantitative information at various points in the system. Your system does not prevent you from making measurements at various intermediate points.
To troubleshoot a system you need to know how the system works. Then you need to make measurements at different parts of the system, and correlate the data with what would make sense for the probed poiints.
You need voltage information and so far I don't see any voltage data. Fundamentally a simple UPS makes use of input voltage to determine its action.
Ask yourself how a UPS works, there are various kinds. Search the Internet for a discussion.
In Google enter the search string:
how does a ups work
Some results are:
http://computer.howstuffworks.com/question28.htm
http://en.wikipedia.org/wiki/Uninterruptible_power_supply
and others.
In posts #2 and #3 I provided you some starting points for troubleshooting.
Why do UPSs randomly change state? If they are in good working condition the reason is the UPS has detected an input voltage that is outside its threshold limits. Not all UPSs of the same model have exactly (precisely) the same voltage thresholds, nor is a threshold likely to be precisely stable over a long time.
It is unlikely you have any UPSs that can run from battery for 40 minutes after a dip in voltage unless the input voltage rises to a level that can keep the battery charged, but not sufficiently high to reconnect the load to the input power source.
.