xptpcrewx
Power System Engineer
- Location
- Las Vegas, Nevada, USA
- Occupation
- Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Where does it say that in the code? And anyway what does that have to do with whether or not the phases are balanced? There's nothing in the code that requires phase balancing. Where in the code does it require the overcurrent devices to be the same rating.
It doesn’t “explicitly” restrict different conductor sizes unless you’re dealing with parallel sets, but you need to look at section 310.14(A)(2) and (A)(3). There is a limit to whatever benefit you’d get from having different sized conductors as part of the same circuit. It’s also very non-standard and I don’t know how you’d assign a feeder rating to the circuit or determine the minimum rating/size in 215.2. Can’t think of a good reason why anyone would want to do this. Perhaps you can tell us? It’s an interesting point though.
Getting back to the main discussion, this is in context of a load calculation regarding a single feeder (I’m guessing 3w) to the equipment and presumably one OCPD.
The line currents are not related to the delta phase currents by 1.732 for unbalanced loading. I provided the actual line currents and phase kVA in my example. It would be reasonable to size the circuit conductors and OCPD based on the largest loaded phase.