You didnt show division by Voltage but yeah you got it.Hi, I'm having a bit of trouble determining how to size the breaker for a 34.5kW heated trash compactor (3ph 480V).
Is it as simple as (34.5kW / 1.732) *1.25 ? This gets me 52A
Thank you
View attachment 2556953
Since nol control panel was mentioned it might be presumptuous but I figured the 125% might apply due to Art 409.Would the 125% even apply as it's probably not considered a continuous load?
If not, then a 45 or 50A breaker would work.