I'm looking to purchase six transformers. Three 167kVA ABB and three 333kVA MEVENCA single phase transformers (Nameplates attached; serials blacked out given that they're not my property, yet).
During the due diligence process, a licensed electrician performed insulation tests and determined that three of the six were defective. However, the EE responsible for the site from which the transformers were pulled is disputing the test results on the basis that he personally oversaw the replacement of the six transformers (now a 2MVA substation) and they were all operating satisfactorily prior to being removed.
In order to provide as much background as possible, I have attached the test results. These were pretty much "informal" tests; they're purpose was to establish whether the transformers worked or not in order to kick off purchase negotiations. In addition, I'd like to add that (and please pardon the redundancy; the nameplates already cover this), the transformers are multi-winging, 2 HV terminals in, 4 LV terminals out (the intention is to connect X2 & X3 in series). They have been stored in a sheltered (albeit, not completely insulated) environment for approximately 5 months; level concrete floors and relative humidity between 50-80% throughout according to my best estimate.
I greatly would appreciate any feedback from this community regarding the following:
1) Would you consider these test results as a reliable indicator as to whether I should move on and look at other transformers (this is with regards to the ones labeled as "bad"). I know that there is a myriad of other tests to be performed on the "good" ones, but would you completely disregard the "bad" ones and look elsewhere?
1) There is always room for human error during testing procedures and, given the fact that these transformers are a "tad" more intricate than your typical overhead distribution equipment, do you believe that there may be an increased possibility that a licensed electrician unfamiliar with these specific transformers may have committed an error?
I can provide as much information as possible if you have any requests for it; I'm simply trying to figure out whether I should have them checked again by another qualified professional or if I should simply avoid the transformers that tested poorly.
Thank you very much for all your help!
During the due diligence process, a licensed electrician performed insulation tests and determined that three of the six were defective. However, the EE responsible for the site from which the transformers were pulled is disputing the test results on the basis that he personally oversaw the replacement of the six transformers (now a 2MVA substation) and they were all operating satisfactorily prior to being removed.
In order to provide as much background as possible, I have attached the test results. These were pretty much "informal" tests; they're purpose was to establish whether the transformers worked or not in order to kick off purchase negotiations. In addition, I'd like to add that (and please pardon the redundancy; the nameplates already cover this), the transformers are multi-winging, 2 HV terminals in, 4 LV terminals out (the intention is to connect X2 & X3 in series). They have been stored in a sheltered (albeit, not completely insulated) environment for approximately 5 months; level concrete floors and relative humidity between 50-80% throughout according to my best estimate.
I greatly would appreciate any feedback from this community regarding the following:
1) Would you consider these test results as a reliable indicator as to whether I should move on and look at other transformers (this is with regards to the ones labeled as "bad"). I know that there is a myriad of other tests to be performed on the "good" ones, but would you completely disregard the "bad" ones and look elsewhere?
1) There is always room for human error during testing procedures and, given the fact that these transformers are a "tad" more intricate than your typical overhead distribution equipment, do you believe that there may be an increased possibility that a licensed electrician unfamiliar with these specific transformers may have committed an error?
I can provide as much information as possible if you have any requests for it; I'm simply trying to figure out whether I should have them checked again by another qualified professional or if I should simply avoid the transformers that tested poorly.
Thank you very much for all your help!