I'm hooking up a starter tomorrow that has an HOA. I have never hooked one up with an HOA feature. The wiring diagram that came with the starter doesn't have the info for that type of set up.

It's a 208V 3P starter with a 208V coil.

There is a "2" and "3" terminal on the top with L1 L2 L3.
A "com" and "X2" on the bottom with T1 T2 T3.

Anyone able to help?
 

kwired

Electron manager
Location
NE Nebraska
Connect incoming power and ougoing power to appropriate terminals. Put your automatic external control in series with the automatic portion of the control circuit. There will be a schematic on the equipment showing where to connect it if you are not certain. Everything else is already done for you at the factory.
 