I would imagine using a breaker below it's rated voltage would increase the AIC. Such as a 480 volt breaker on a 208 circuit. Is there any way this increase in AIC can be applicable?
 
I would imagine using a breaker below it's rated voltage would increase the AIC. Such as a 480 volt breaker on a 208 circuit. Is there any way this increase in AIC can be applicable?
It is done every day by manufacturers. Take a look at the labels on any industrial breaker (they are usually large enough to read) or look in their catalogs.
 
Yes, and the old line AB breakers were brand labeled Westinghouse, then by virtue of the buyout, Eaton. It was Eaton that I had the argument with on AIC ratings when I was with an OEM. AB not longer brand labels the Eaton breakers though.
I think they are now made by ABB.

I don't know if UL allows this anymore but it used to be that if you wanted a breaker that could be reverse fed it had to have non-interchangeable trip elements. I never understood why, there seems to be no obvious reason for this, but some MCCB manufacturers would install regular interchangeable trip elements and then put a seal over it and then UL would allow them to market it as a MCCB that could be reverse fed.

I also have been told that some IEC contactors that are labeled with lower ratings for some models in the same frame size are internally identical.
 
I don't know if UL allows this anymore but it used to be that if you wanted a breaker that could be reverse fed it had to have non-interchangeable trip elements. I never understood why, there seems to be no obvious reason for this, but some MCCB manufacturers would install regular interchangeable trip elements and then put a seal over it and then UL would allow them to market it as a MCCB that could be reverse fed.
They don't want you exposing live parts when you pull out the trip unit.
 