A brand new one just burned up. The question is why?
The unit arrived set up for 480 volts three phase. The application required 220 three phase.
I correctly set up the windings taps for 220 volts. (Verified by the tech that came out to see the burned out unit.)
The problem is that upon setting this up for a different voltage I overlooked a setting on the AVR.
It is the Leroy Somer, A.V. R. R438 the setup instructions for this thing are at this link;
http://www.leroy-somer.com/documentation_pdf/alternateurs_pdw/notices_pdf/3971e_en.pdf
The system is AREP.
On page 4 you will see terminals 220, and 380 (marked for voltage) This appears to be the voltage sensing circuit. I failed to change the connection from 380 to 220. that was all anyone could find wrong with setup.
I'm being told that the windings were "set up" for 220, but the AVR thought it was supposed to be 380+. Therefore it overexcited the unit to death trying to bring the voltage up to the expected 380+.
Is it possible that this incorrect setting could cause the unit to self destruct?
This thing burned up so bad it is not repairable!
I would of thought that the worst case would be blowing the AVR.
Thanks
Rick
The unit arrived set up for 480 volts three phase. The application required 220 three phase.
I correctly set up the windings taps for 220 volts. (Verified by the tech that came out to see the burned out unit.)
The problem is that upon setting this up for a different voltage I overlooked a setting on the AVR.
It is the Leroy Somer, A.V. R. R438 the setup instructions for this thing are at this link;
http://www.leroy-somer.com/documentation_pdf/alternateurs_pdw/notices_pdf/3971e_en.pdf
The system is AREP.
On page 4 you will see terminals 220, and 380 (marked for voltage) This appears to be the voltage sensing circuit. I failed to change the connection from 380 to 220. that was all anyone could find wrong with setup.
I'm being told that the windings were "set up" for 220, but the AVR thought it was supposed to be 380+. Therefore it overexcited the unit to death trying to bring the voltage up to the expected 380+.
Is it possible that this incorrect setting could cause the unit to self destruct?
This thing burned up so bad it is not repairable!
I would of thought that the worst case would be blowing the AVR.
Thanks
Rick