Here is what I plan on doing.
I have a 2" U/G conduit to an outbuilding.
I will have 3 feeder conductors for a 100 amp sub feed (3 THWN-2).I will have 2 travelers and a switch leg (12thwn)for one fixture controlled from outbuilding and house both.
J
I will have 1 neutral, 1 switch leg, 1 power , and 2 travelers(12thwn) for another fixture controlled from outbuilding and house both.
Do I figure all 8 of the number 12 as ccc's, or just 6?
If 6, that will make a total of 9 ccc's and I can use 70% for deration.
That will give me 91 amps on the #3's and 21 amps on the #12's.
Is this correct?
Thanks.