I ran into this situation in Iraq on a site we are inspecting. A 3-pole MTS was fed from the utility transformer and by a back up generator. There is a 4wire cable coming from the transformer, and a 4 wire cable coming from the generator, and the generator is bonded. The transformer has its own ground rod.
Inside the MTS, the neutral bus is isolated, and the neutrals land on it, as well as the connection to the ground rod. There is another wire connecting the case to the same ground rod. This wire is attached to the bolt that holds the hinge on the door. There are no wires landed on the grounding bus.
I think this is in violation of 250.6(A), Arrangement to prevent objectioanble current. I feel a 4-pole MTS is needed, and the neutals should be switched.
I would greatly appreciate any input anyone has, I am not very familiar with transfer switches. Thanks a lot!
Inside the MTS, the neutral bus is isolated, and the neutrals land on it, as well as the connection to the ground rod. There is another wire connecting the case to the same ground rod. This wire is attached to the bolt that holds the hinge on the door. There are no wires landed on the grounding bus.
I think this is in violation of 250.6(A), Arrangement to prevent objectioanble current. I feel a 4-pole MTS is needed, and the neutals should be switched.
I would greatly appreciate any input anyone has, I am not very familiar with transfer switches. Thanks a lot!