I was looking at a mfg. site for amp rating on generators and need some help with how they came up with the rating.
120/208v 3ph 30kw pf.8 the mfg. has 104 amp
my numbers came out at 83.3
30000/208/1.73
30000/208= 144.2 144.2/1.73= 83.3
What am I doing wrong or dose the PF come into play and if so how?