150830-0027 EDT
junkhound:
How do you avoid burning out a relay coil without some explicit current limiting?
Using some round numbers assume that a 24 V 30 VA transformer can supply about 1 A. But for calculation purposes use 0.5 A in a 50 ohm resistor and the power dissipation is 1/4 of 50 = 12.5 W. This almost certainly would burn out a GE RR relay coil. On my system I limit steady-state current such that coil power is about 0.2 W in a single coil.
.
junkhound:
How do you avoid burning out a relay coil without some explicit current limiting?
Using some round numbers assume that a 24 V 30 VA transformer can supply about 1 A. But for calculation purposes use 0.5 A in a 50 ohm resistor and the power dissipation is 1/4 of 50 = 12.5 W. This almost certainly would burn out a GE RR relay coil. On my system I limit steady-state current such that coil power is about 0.2 W in a single coil.
.