Yep, you have some overdutied equipment that should be replaced.
Square D started putting labels on the front of their I-Line breakers around 1985. Prior to that the higher AIC 480V devices often had colored handles.
Your main breaker is more than 40 years old, has it ever been tested?
Well not exactly sure what you mean by tested. After starting this thread, I did exercise the breaker And found that the A pole is not opening. Same client had the same problem with the same breaker at another building. Not sure of that is coincidence or there was a flaw with these breakers. So considering all that, the gear needs to be replaced.