I have been studying several of the subjects I lack knowledge in, and one of them is transformers.
I have a book on transformers Im going thru and always look at the nameplate ratings on them when I get the chance.
I came across one today that feeds 2 dwelling units and a shop all with single phase power that is supplied by the utility company.
the nameplate reads
37.5kva 2% imp
12470GRDY/7200 primary
240/120 secondary
1- In a wye system, phase volt * 1.732 = line volts So Im guessing thats the primary 7200*1.732=12470?
2-Is it a common or standard that utility use 3phase xformers to supply single phase dwellings?
3-what does the "GRDY" signify in the nameplate rating
Thanks alot for any input