Donald Blake
Member
- Location
- Tampa Bay FL
An engineer / Home owner who has built his own house and hired the GC and Electrical subs ect... Has bought the Ideal 65-165 circuit analyzer and has gone to the last receptacle outlet on the general branch circuits and has determined based on a 20 amp 80% load of 16 amps that there is a voltage drop code violation and is holding back payment. These branch circuits only have 7-10 outlets on a 20 amp #12 wire. According to the Ideal tester you can't exceed more than 60 -70 feet before you exceed the 3%. When you exceed 90 feet at the 16 amp test you will exceed a 5% drop. I know that this is only a recommendation and not a mandatory rule in the code. This guy is not interested in what the inspectors say because he knows that he understands more than they do, by the way he is also not paying the GC for something. This electrical contractor is not able to deal with a long court case and this guy is very wealthy and has no problems with sticking it to this electrical contractor.