Someone brought this question to me, and Im a little unsure on the answer.
Here is goes:
------------------------------------------------------------------
The following question is regarding the electric motor specified below:
150 HP, Three Phase, 60HZ
444T Frame, 1750 RPM, Code F
460 Volts, 180 FL Amperes.
Continuous Duty, 40C Ambient.
Q: What is the maximum allowable motor running overcurrent protection trip setting without using exceptions?
A.) 207 Amps
B.) 189 Amps
C.) 198 Amps
D.) 225 Amps
----------------------------------------------------------------------------------
When working this problem I sized the overloads based on full load current times 125% due to the motor meeting the 40C Ambient temp. Giving me an answer of 225 Amps. The workbook shows the answer as 207Amps. They get that answer from sizing overloads using 115%. Why do they use this number though ? Im a little confused.
Here is goes:
------------------------------------------------------------------
The following question is regarding the electric motor specified below:
150 HP, Three Phase, 60HZ
444T Frame, 1750 RPM, Code F
460 Volts, 180 FL Amperes.
Continuous Duty, 40C Ambient.
Q: What is the maximum allowable motor running overcurrent protection trip setting without using exceptions?
A.) 207 Amps
B.) 189 Amps
C.) 198 Amps
D.) 225 Amps
----------------------------------------------------------------------------------
When working this problem I sized the overloads based on full load current times 125% due to the motor meeting the 40C Ambient temp. Giving me an answer of 225 Amps. The workbook shows the answer as 207Amps. They get that answer from sizing overloads using 115%. Why do they use this number though ? Im a little confused.