Is the info correct? If yes, I will go back and read closer later.
IMO yes.
Is the info correct? If yes, I will go back and read closer later.
Are we supposed to interpret "running overcurrent protection" as meaning overload protection?
If so there is no additional allowance for motor starting. To that extent the question is poorly written, using terms that the NEC does not use or define.
Overcurrent protection (short circuit and ground fault protection) is where you can definitely increase the nominal value to allow starting.
IMO yes.
I think i catching on. Just reading "ambient temperature" and "temperature rise", I can tell you there is a difference. I just assumed when they were referring to temperature when dealing with a motor, that they were referring to the rise. So, if it states ambient temperature, its pointless since the temperature around the motor is useless.