memyselfandI
Senior Member
- Location
- Hampton Roads, Virginia
I have a 480V 3ph 4w 1000A service with a underground feed of 2 sets of 500mcm CU. I don't know what the calculated load was at the time of construction, but apparently is was sufficient enough to warrant a 1000A service.
230.90(A) reads that "Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor." If the breaker has terminals rated at 75*Cel, how can one get away with only running 2 sets of conductors when they would be rated at 380A each? IMO this is undersized and a third set needs to be pulled to satisfy this requirment.
230.90(A) reads that "Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor." If the breaker has terminals rated at 75*Cel, how can one get away with only running 2 sets of conductors when they would be rated at 380A each? IMO this is undersized and a third set needs to be pulled to satisfy this requirment.