We have 4 customers all within a couple miles of each other who are claiming that their PV systems are causing AFCI load breakers unrelated to the PV system in their houses to trip. One of the customers has told us that his breakers are tripping at night when the PV system is (obviously) not producing. What the installations have in common besides geographic proximity is that they are on the same utility, the same electrician wired all these homes, all the panels and breakers are Square D, and in all cases the PV is interconnected in the MDP while the breakers that are tripping are in subpanels. And of course we built all the PV systems.
The systems are arrays of Sunpower modules with microinverters using their proprietary powerline communication for monitoring. We have several hundred systems in the field built on this same basic design, and these four customers are the only ones reporting this problem, if there is a problem.
The obvious first thing to do was to turn off the PV systems for a couple of weeks and see if the breakers stop tripping; all four customers did that and reported that they had no trips during that time but that the trips started up again when they turned their PV systems back on. Is something in the powerline communication that could indicate to the AFCI breakers that there is an arc fault, even though it's on another breaker in another panel? If so, why is it only happening in only these particular systems out of the hundreds of the same ilk we have built?
I've got nothing. You?