- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
This is just an FYI. I wanted to pass on an odd situation that I just discovered. The oddity is revealed at the end of this message.
A friend and the electrician he hired have been scratching their heads over a problem with a feeder to a 4-circuit sub-panel in his detached garage. I don't have all the details, but I gather that breakers have been tripping (in the house or in the garage or both, I'm not sure), and that the electrician suspects a short in the underground portion of the conduit run. There was a 2-pole, 20 amp breaker in the main panel to feed the garage, and the only action taken so far is to replace it with a 2-pole 30 amp breaker. I did not personally verify that the conductors were #10, but I trust the electrician did.
I told my friend that he would be better off supplying the sub-panel with a 50 amp breaker, just to ensure there is capacity for whatever he wants to put there. Then I told him I would look up the required sizes of conductors and conduit, since I didn't want to go by memory. So I check Table 310.16 this morning, and confirm my guess that a #8 would serve. Then I check Table 250.122, and see that a #10 EGC would serve.
Next, I think about the probable distance of the run. It might be close to, or even more than, 100 feet. So I then think of recommending an up-size, due to voltage drop considerations. That means a #6 conductor. It also means that the EGC would have to be upsized from a #10 to a #8. That is not because of Table 250.122, but rather because of article 250.122(B).
Now the plot sickens ? no I mean thickens. What if I had suggested that the sub-panel be supplied by a 60 amp breaker? (This presumes it is rated at 60 amps, or would be replaced by a panel that is rated at least that high). Now I need to use #6 conductors, but can still use a #10 EGC.
In summary, the choices are:
A friend and the electrician he hired have been scratching their heads over a problem with a feeder to a 4-circuit sub-panel in his detached garage. I don't have all the details, but I gather that breakers have been tripping (in the house or in the garage or both, I'm not sure), and that the electrician suspects a short in the underground portion of the conduit run. There was a 2-pole, 20 amp breaker in the main panel to feed the garage, and the only action taken so far is to replace it with a 2-pole 30 amp breaker. I did not personally verify that the conductors were #10, but I trust the electrician did.
I told my friend that he would be better off supplying the sub-panel with a 50 amp breaker, just to ensure there is capacity for whatever he wants to put there. Then I told him I would look up the required sizes of conductors and conduit, since I didn't want to go by memory. So I check Table 310.16 this morning, and confirm my guess that a #8 would serve. Then I check Table 250.122, and see that a #10 EGC would serve.
Next, I think about the probable distance of the run. It might be close to, or even more than, 100 feet. So I then think of recommending an up-size, due to voltage drop considerations. That means a #6 conductor. It also means that the EGC would have to be upsized from a #10 to a #8. That is not because of Table 250.122, but rather because of article 250.122(B).
Now the plot sickens ? no I mean thickens. What if I had suggested that the sub-panel be supplied by a 60 amp breaker? (This presumes it is rated at 60 amps, or would be replaced by a panel that is rated at least that high). Now I need to use #6 conductors, but can still use a #10 EGC.
In summary, the choices are:
- #6 conductors, 50 amp breaker, #8 EGC, or
- #6 conductors, 60 amp breaker, #10 EGC