Hi-fi equipment and UL?

Status
Not open for further replies.

Speedskater

Senior Member
Location
Cleveland, Ohio
Occupation
retired broadcast, audio and industrial R&D engineering
In a residential situation does plug-in hi-fi equipment require a safety label or mark?
What about small plug-in appliances?
 
NRTL listing is not “required” by code for anything that is plugged in, because the Code is only about permanent installations and construction standards. If you want to risk your life on something that the manufacturer didn’t think would pass testing to any standards that apply here, so they didn’t even try (or tried and failed) that’s up to you.

In SOME cases, homeowner insurance policies may have “fine print” statements to the effect of giving them an out from paying for damages as the result of a fire caused by unlisted devices. They would have to prove it of course, but that increases your risks in deciding to purchase the devices.

NRTL listings also help protect the resellers of these devices from indemnity over manufacturer defects. So if you buy something from a brick-and-mortar store and it starts a fire, the store can deflect blame by saying “It was a listed device, we did our due diligence so talk to the manufacturer”. That’s why you will not see unlisted devices being sold that way. But when you buy them on-line, the on-line seller is just “facilitating” a transaction between you and the cheap crap manufacturer or dealer, usually in China. If something goes wrong, the on-line seller says “Caveat emptor”, an ancient legal precept that means “buyer beware”; it is incumbent on the buyer to understand what they are buying and what risks are involved. Then if you go after the Chinese supplier, they are shielded by their government against liability claims. You end up screwed and holding the ashes of your disappointment.
 
NRTL listing is not “required” by code for anything that is plugged in, because the Code is only about permanent installations and construction standards. If you want to risk your life on something that the manufacturer didn’t think would pass testing to any standards that apply here, so they didn’t even try (or tried and failed) that’s up to you.
...
While I agree that is how the code should work, I don't think CMP 17 understands that.
422.6 Listing Required.
All appliances supplied by 50 volts or higher shall be listed.
There are a number of rules in 422 that apply to cord and plug connected appliances.

It is my opinion that much of Article 422 is outside the scope of the NEC an unenforceable, but AHJs do not see it that way.
 
What about AHJ's and safety markings?
Kind of comes down to what are they an AHJ of? Typical EI is enforcing NEC which their inspections will usually stop at the receptacle with most plugged in items, presuming it is an item that is otherwise allowed to be plugged in.

Insurance companies, OSHA, and the like may have more than just NEC they take into consideration.
 
Some jurisdictions have separate local rules requiring listing. City of LA is one.
When they inspect do they confiscate non listed items?

Do they check to see if an item marked as listed actually has a valid listing?

I can see being more particular on items that are fastened in place, but there is a lot of consumer items out there that plug in and many probably are not listed.
 
When does an AHJ even see a plugged in appliance? As I said, the NEC is about construction standards. I have always interpreted those rules to mean any appliance INCLUDED IN AN INSPECTION, which might mean plugged in appliances sold as part of a newly built home that has to pass a final inspection, so like a range, microwave, etc. Why would an inspector be there to see HiFi equipment plugged into an outlet? That would make them REALLY busy after the Holidays…

Even during a room addition where there was existing equipment plugged in, the only time I’ve seen an AHJ walk the rest of the house was to look for smoke detectors. So I suppose that technically 422.6 applies, but not in a way that will matter to the OP (from a Code standpoint).
 
Status
Not open for further replies.