Contracted to add several 208v 1ph circuits for new HVAC equipment in a 100+ year old funeral home.
Went to take a look @ the job and found a 208/120v hi-leg delta configured service. Checked a fairly current (installed in 2000) Siemens 400a pnl with plenty of "B" slots open (imagine that!). The available hi leg slots would be perfect for the new circuits. Noted Siemens "BL" ckt brkrs. No problem.....I think.
It's time to buy the breakers. I go to the supply house and ask for Siemens 1pole, 20amp "BL" breakers. The guy brings the breakers to the counter. I happen to look at the breakers and notice they're rated 120/240v. I tell him that I can't use slash rated breakers, I need to use them on a hi-leg and that they need to be rated 240v. He looks at me as if I have 2 heads and informs me that they don't come in straight 240v and shows me in the Siemens catalog. He thinks I'm looking for the wrong breaker and I think so also.
I return to the job to confirm my selection. To my surprise, I notice that the name plate on the panel specifies 120/208Y(not delta), 3p, 4w, 400a. No wonder I can't find breakers! I'm thinking that the contractor that installed the panel selected the wrong equipment... what a mistake!
In any event, I switched some breakers around and used 2pole breakers rated at 240v for the new equipment.
Any of you guys run across this situation in your travels?
See any problems with the solution?
Bob
Went to take a look @ the job and found a 208/120v hi-leg delta configured service. Checked a fairly current (installed in 2000) Siemens 400a pnl with plenty of "B" slots open (imagine that!). The available hi leg slots would be perfect for the new circuits. Noted Siemens "BL" ckt brkrs. No problem.....I think.
It's time to buy the breakers. I go to the supply house and ask for Siemens 1pole, 20amp "BL" breakers. The guy brings the breakers to the counter. I happen to look at the breakers and notice they're rated 120/240v. I tell him that I can't use slash rated breakers, I need to use them on a hi-leg and that they need to be rated 240v. He looks at me as if I have 2 heads and informs me that they don't come in straight 240v and shows me in the Siemens catalog. He thinks I'm looking for the wrong breaker and I think so also.
I return to the job to confirm my selection. To my surprise, I notice that the name plate on the panel specifies 120/208Y(not delta), 3p, 4w, 400a. No wonder I can't find breakers! I'm thinking that the contractor that installed the panel selected the wrong equipment... what a mistake!
In any event, I switched some breakers around and used 2pole breakers rated at 240v for the new equipment.
Any of you guys run across this situation in your travels?
See any problems with the solution?
Bob