Hey All,
My first big commercial job (well, big for me. Peanuts to some of you, I'm sure) There are 50 100W Metal Halide recessed lights in a walkway canopy (120V). The ballast says 1.1A running, 2.2A startup. How do I size this circuit? Do I need to size it for 2.2A each even though it only draws that for a few seconds? I can't seem to find any reference to this ballast start-up scenario in Art 410 or 220.
My first big commercial job (well, big for me. Peanuts to some of you, I'm sure) There are 50 100W Metal Halide recessed lights in a walkway canopy (120V). The ballast says 1.1A running, 2.2A startup. How do I size this circuit? Do I need to size it for 2.2A each even though it only draws that for a few seconds? I can't seem to find any reference to this ballast start-up scenario in Art 410 or 220.