High bay disconnects

Status
Not open for further replies.

slc410

Electrician
Location
Madison wi
Occupation
Electrician
Is there still a requirement for a disconnect for the new LED high bay fixtures like the UFO style that are popular now? We got a new Lithonia fixture package for a business and it does not come with the incorporated quick disconnects within the fixture junction and so I was wondering if I need to install a twist lock in the four square box feeding the fixture. A code reference would be nice as well. Thanks all
 
I believe 410.62 is likely to require the entire fixture to be cord & plug so the ballast disconnect question may be moot.
 
Status
Not open for further replies.
Top