We use Fluke 1507 Insulation Testers. The POCO had the transformer fuse pulled, with meter out when I got there and were waiting for me. The customer owns and is responsible for the lateral. The owner had turned the Main breaker off on his panel. Service was 4/0 4/0 2/0 direct bury Al. First check was from meter can load lugs to pole ground. Reading was .010 meg with a voltage maintained at 14v. Test range was 500 volts. I removed all the load wires at the meter can, removed the neutral in the service panel and confirmed the main was off. Readings were the same. Faults were where whoever buried a private propane line years ago and had cut through the lateral. Two splices on each side for all three conductors.
Readings after repair were >550 M @ 526 VDC.
The buried maker tape didn’t appear to have prevented any damage