Did you happen to notice that your unit has a single phase motor in there too? It's drawing 3.1A at full load, SINGLE phase 208-240V. No indication of which phases it is connected to, but my guess is L2 is one of them, and that is making your imbalance worse.
"Roll" your conductors feeding this and see if the imbalance follows the roll. Rolling means move L1 to L2, L2 to L3, L3 to L1; rotation remains the same, but you shift which line goes to where. If the unbanned stays exactly the same, it's an internal issue in the A/C unit. If the issue changes, in in the source. Rolling is also a first strategy for mitigating it, you may end up taking advantage of slight differences in internal natural resistances/ impedance in the motors.