High current on the high leg

Status
Not open for further replies.
Did you happen to notice that your unit has a single phase motor in there too? It's drawing 3.1A at full load, SINGLE phase 208-240V. No indication of which phases it is connected to, but my guess is L2 is one of them, and that is making your imbalance worse.

"Roll" your conductors feeding this and see if the imbalance follows the roll. Rolling means move L1 to L2, L2 to L3, L3 to L1; rotation remains the same, but you shift which line goes to where. If the unbanned stays exactly the same, it's an internal issue in the A/C unit. If the issue changes, in in the source. Rolling is also a first strategy for mitigating it, you may end up taking advantage of slight differences in internal natural resistances/ impedance in the motors.

Tomorrow first thing, I'll report back our findings. Thank you!


Sent from my iPhone using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
L1-ground 118
L2-ground 220
L3-ground 119

L1-L2 - 249V
L1-L3 - 238V
L2-L3- 250V

Current draw
L1 23.9
L2 32.5
L3 25.4



Sent from my iPhone using Tapatalk
Is the AC units the only load using the third phase (high leg)?

How much other load is there on the 120/240 "lighting" pot?

I still think it may be possible the lighting pot maybe is heavily loaded dragging it's voltage down some, but the stinger pot is not really that heavily loaded for it's rating and isn't being dragged down and that is why there is such an imbalance

You seem to have near 250 volts from L2 to each other line, normal high leg voltage if line to line voltages is 250 would be about 216-217 volts getting close to your measured 220, but if the lighting pot is being dragged down to 238 then 118-119 to ground on those would be expected.

You can't expect current balance in a three phase motor if input voltages aren't balanced.

Add: then after prolonged usage at unbalanced currents, the condition of the motor possibly deteriorates and the unbalance gets even worse.
 
Last edited:

JFletcher

Senior Member
Location
Williamsburg, VA
Is the AC units the only load using the third phase (high leg)?

How much other load is there on the 120/240 "lighting" pot?

I still think it may be possible the lighting pot maybe is heavily loaded dragging it's voltage down some, but the stinger pot is not really that heavily loaded for it's rating and isn't being dragged down and that is why there is such an imbalance

You seem to have near 250 volts from L2 to each other line, normal high leg voltage if line to line voltages is 250 would be about 216-217 volts getting close to your measured 220, but if the lighting pot is being dragged down to 238 then 118-119 to ground on those would be expected.

You can't expect current balance in a three phase motor if input voltages aren't balanced.

Add: then after prolonged usage at unbalanced currents, the condition of the motor possibly deteriorates and the unbalance gets even worse.

That thought crossed my mind too, with either a lot of kitchen equipment running or site lights at night.

The 1ph motor would account for some imbalance but not what the OP has. Blowing compressor motors over the years as the OP said seems to me to be a power problem (unless they are all underwired...).

I fail to see how a high leg voltage of even 240V to g/n would matter when all of the line to line voltages are right on the money. If I had to take a wag, I'd say there is an overload on the larger pot with single phase loads.

A power logger may be more helpful than instantaneous readings.

On an aside, I saw a Carrier 64Ton unit (2 compressors) blow 3 compressors in less than 2 years due to a leak in the system. HVAC guy recharges it, more oil, which eventually formed a slug that hydraulically locked the compressors, and metal carnage ensued. Nothing to do with the electrical at all.
 
Here is our recorded voltage and amperage readings after a new compressor install on unit 1.

The following was provided by our HVAC Group:
June 6, 2017

86 degrees outside

PM heavy load

*Single phase condenser fan motor moved to L1 and L3



L1 to ground- 118.7 volts

L2 to ground- 216.9 volts

L3 to ground- 119.2 volts



L1-L2- 245 volts

L1-L3- 239 volts

L2-L3- 240 volts



Amps

L1- 21.2

L2- 27.5

L-3 20.2

*FULL LOAD AMPS OF THE COMPRESSOR IS 25

***The refrigerant charge was left at 80% of the total charge in order to keep the high leg at 27.5. The end result is the equipment is not running at full capacity. We know that as the outside temperature increases the amperage will increase across the board.



Trane says “any amperage unbalance is unacceptable, and the nameplate FLA can never be exceeded, but the voltage can be unbalanced by 2%”. In the real world, most motor experts say that anything below 10% amperage unbalance is acceptable.



Check my math and let me know.

Average amps = (21.2+27.5+20.2) /3= 22.97

(High reading 27.5 minus average 22.97) /average 22.97 x 100 = 19.7% unbalanced



If this is correct, we have to get the unbalance between 0 and 10% with a full refrigerant charge.




Sent from my iPhone using Tapatalk
 

kwired

Electron manager
Location
NE Nebraska
L1-ground 118
L2-ground 220
L3-ground 119

L1-L2 - 249V
L1-L3 - 238V
L2-L3- 250V

Current draw
L1 23.9
L2 32.5
L3 25.4



Sent from my iPhone using Tapatalk
Gave those numbers some more thought. I think I mentioned before, or at least something to effect that if line to line voltages were all 250 volts then A and C to neutral would be 125 and B to neutral would be 216.5.

Now draw voltage down from other loads in the facility between A and C so that you have 238 between them and ~118-119 to neutral but leave load on B minimal enough you still have 250 from B-C. Drawing out that half of the delta with 119 on one side, 250 for hypotenuse leaves the other side at 219.86, that is why the high leg voltage is as high as it is.

What doe service voltage readings look like, both at minimal demand and at peak demand?

What is kVA rating of the transformers in the bank and how much load is connected - especially at moderate to high demand periods?

I still am convinced the size of the "lighting pot" possibly needs increased, or maybe if the stinger pot has the ability to change supply tap to lower output voltage so it better matches the loaded lighting pot. If POCO can't/won't do anything maybe an autotransformer in the high leg to better balance voltages.
 