mreeves007
Member
I have a two concerns with the use of a high impedance grounded generator.
NEC 250.36 states this is premitted where four conditions are met. The one I have a question about is the fouth concern: Line-to-neutral loads are not served. Our current configuration has a 480VAC generator feeding 6 isolation transformers that control various functions of a crane (travel, hoist, rotate, etc.). One of the transformers feeds lighting circuit and computers where the neutral of the load side is grounded (y connected) and provides the return path neutral for the circuit. The generator is also provided with a high impedance neutral.
Based on NEC 250.36, this is not allowed. Our concern is to limit the amount of fault current during a phase to ground fault. There is a ground fault relay across the generator netural impedance so that when a fault is detected, it removes all power from the crane. This is safer than having a solidly grounded generator which would allow up to 1200A of fault current before a breaker trips. The use for the 120V (line-to-neutral) system is to provide power for lights and the drive systems that operate the crane. These are necessary.
Thus my first question is "why are line-to-neutral load not allowed on a high impedance grounded generator?" NEC does not provide any explanation for this.
My second question is "for the other transformers that do not have a neutral, should the load side (y connected) be grounded?" Currently they are ungrounded.
Thanks
Matthew
NEC 250.36 states this is premitted where four conditions are met. The one I have a question about is the fouth concern: Line-to-neutral loads are not served. Our current configuration has a 480VAC generator feeding 6 isolation transformers that control various functions of a crane (travel, hoist, rotate, etc.). One of the transformers feeds lighting circuit and computers where the neutral of the load side is grounded (y connected) and provides the return path neutral for the circuit. The generator is also provided with a high impedance neutral.
Based on NEC 250.36, this is not allowed. Our concern is to limit the amount of fault current during a phase to ground fault. There is a ground fault relay across the generator netural impedance so that when a fault is detected, it removes all power from the crane. This is safer than having a solidly grounded generator which would allow up to 1200A of fault current before a breaker trips. The use for the 120V (line-to-neutral) system is to provide power for lights and the drive systems that operate the crane. These are necessary.
Thus my first question is "why are line-to-neutral load not allowed on a high impedance grounded generator?" NEC does not provide any explanation for this.
My second question is "for the other transformers that do not have a neutral, should the load side (y connected) be grounded?" Currently they are ungrounded.
Thanks
Matthew