High leg delta and corner grounded delta

Merry Christmas

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
The high-leg, yes, in the sense that the opposite (main) winding needs a center tap to be the neutral.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Can you please explain that better still new to this subject regarding high leg delta and corner grounded systems thanks
Simply, what fixes the voltage to ground from any given terminal is which terminal one chooses to intentionally ground.

A high-leg delta has as a high leg because of the voltage between that terminal and the grounded neutral.

A corner-grounded delta has two terminals with line-to-ground voltages same as the line-to-line voltage.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
The secondary of a transformer is only magnetically coupled to the primary. There is no wiring connection from the primary to the secondary coils ever.

This is an old post from Larry Fine that I have used in the past that I have used to explain the grounded/neutral conductor. His example does not use three phase but it might be helpful for your question. https://forums.mikeholt.com/threads/understanding-the-neutral-conductor.140537/
 
Just to emphasize: how many terminals an electrical system has is unrelated to if or which terminal is grounded.

There are probably a few exceptions (well actually quite a few if you get into medium voltage transformers built for an MGN wye system) but usually a terminal is not "internally grounded" where its buried in the guts of a transformer. Typically it's brought out just like the other terminals , but where a given terminal is very commonly grounded, the manufacturer often provides a removable strap.
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
The secondary of a transformer is only magnetically coupled to the primary. There is no wiring connection from the primary to the secondary coils ever.

This is an old post from Larry Fine that I have used in the past that I have used to explain the grounded/neutral conductor. His example does not use three phase but it might be helpful for your question. https://forums.mikeholt.com/threads/understanding-the-neutral-conductor.140537/
This make it a bit easier to understand


So for a corner grounded you would have a double lug one for power and one to ground let's say the b phase

But for a high leg how would you center tap the between phases

This is new to me and confusing also I'm a visual learner so picture and diagrams help a lot thanks for the help
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
But for a high leg how would you center tap the between phases
Simple. The neutral of a high-leg delta is identical to the neutral of a 120/240v 1ph secondary.

Before I go on, let me know if you understand that concept, as explained in the link posted above.
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
Simple. The neutral of a high-leg delta is identical to the neutral of a 120/240v 1ph secondary.

Before I go on, let me know if you understand that concept, as explained in the link posted above.
Yes I understand how a 120v/240v transformer works

Since you said the high leg delta works the same my question is dose the manufacturer tap the coils for you and you just terminate at the neutral lug

And how would you wire the corner grounded method in the field

Thanks again its greatly appreciated
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Since you said the high leg delta works the same my question is dose the manufacturer tap the coils for you and you just terminate at the neutral lug
Yes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.

And how would you wire the corner grounded method in the field
Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
Yes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.


Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)
What's do you mean by one secondary every transformer only has one secondary
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
Yes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.


Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)
So in a corner grounded system there is no neutral only 3phase like in a 3 phase motor
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
So in a corner grounded system there is no neutral only 3phase like in a 3 phase motor
Yes. In a corner ground there is no neutral, but there is a grounded conductor. We toss around the word neutral on the job when it is more properly called the grounded conductor.
3214_corner_grounded_delta_diagram.jpg
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
Yes. In a corner ground there is no neutral, but there is a grounded conductor. We toss around the word neutral on the job when it is more properly called the grounded conductor.
3214_corner_grounded_delta_diagram.jpg
So in a corner grounded system you can't pull 120v but since one of the phases is grounded it provides us with ground fault protection
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
So in a corner grounded system there is no neutral only 3phase like in a 3 phase motor
Basically. You choose one line to become the grounded phase, unless it's supplied with one.

As with a 1ph neutral, you treat it as a line conductor, other than OCP, such as not re-bonding it.
 