When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
The high-leg, yes, in the sense that the opposite (main) winding needs a center tap to be the neutral.When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
Can you please explain that better still new to this subject regarding high leg delta and corner grounded systems thanksThe high-leg, yes, in the sense that the opposite (main) winding needs a center tap to be the neutral.
Simply, what fixes the voltage to ground from any given terminal is which terminal one chooses to intentionally ground.Can you please explain that better still new to this subject regarding high leg delta and corner grounded systems thanks
The secondary of a transformer is only magnetically coupled to the primary. There is no wiring connection from the primary to the secondary coils ever.When it comes to high leg delta and corner grounded Delta is there a special transformer that's wired internally for these types of connections ??
That's so funny! I actually thought about posting a link to that here. Thank you.This is an old post from Larry Fine that I have used in the past that I have used to explain the grounded/neutral conductor.
This make it a bit easier to understandThe secondary of a transformer is only magnetically coupled to the primary. There is no wiring connection from the primary to the secondary coils ever.
This is an old post from Larry Fine that I have used in the past that I have used to explain the grounded/neutral conductor. His example does not use three phase but it might be helpful for your question. https://forums.mikeholt.com/threads/understanding-the-neutral-conductor.140537/
Simple. The neutral of a high-leg delta is identical to the neutral of a 120/240v 1ph secondary.But for a high leg how would you center tap the between phases
Yes I understand how a 120v/240v transformer worksSimple. The neutral of a high-leg delta is identical to the neutral of a 120/240v 1ph secondary.
Before I go on, let me know if you understand that concept, as explained in the link posted above.
What's even funnier is the last time I posted a link to it was during your hiatus and I described you as a member who had stopped posting and you replied "I'm back" that day.That's so funny! I actually thought about posting a link to that here. Thank you.
Yes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.Since you said the high leg delta works the same my question is dose the manufacturer tap the coils for you and you just terminate at the neutral lug
Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)And how would you wire the corner grounded method in the field
What's do you mean by one secondary every transformer only has one secondaryYes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.
Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)
So in a corner grounded system there is no neutral only 3phase like in a 3 phase motorYes. Either only one secondary has a center tap, or they only provide a neutral terminal for one of them.
Simply, you select one line, ground it, color it white or gray, and don't put a fuse in it. (3p breaker okay)
Yes. In a corner ground there is no neutral, but there is a grounded conductor. We toss around the word neutral on the job when it is more properly called the grounded conductor.So in a corner grounded system there is no neutral only 3phase like in a 3 phase motor
Pretty sure he means only one secondary coil.What's do you mean by one secondary every transformer only has one secondary
So in a corner grounded system you can't pull 120v but since one of the phases is grounded it provides us with ground fault protectionYes. In a corner ground there is no neutral, but there is a grounded conductor. We toss around the word neutral on the job when it is more properly called the grounded conductor.
Correct.So in a corner grounded system you can't pull 120v but since one of the phases is grounded it provides us with ground fault protection
I meant each of the three secondaries of a 3ph transformer.What's do you mean by one secondary every transformer only has one secondary
Basically. You choose one line to become the grounded phase, unless it's supplied with one.So in a corner grounded system there is no neutral only 3phase like in a 3 phase motor