@LarryFine

You guys helped me understand it a bit better but I'm still not fully grasping it ,would

Mike holts book on grounding and bonding

Or
Soares book on grounding and bonding

Help me understand this better

Thanks again
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
@LarryFine

You guys helped me understand it a bit better but I'm still not fully grasping it ,would

Mike holts book on grounding and bonding

Or
Soares book on grounding and bonding

Help me understand this better

Thanks again
I used Soared during my career.
But I think this is an overall electrical theory issue, not simply grounding/bonding, so you should look into transformers/systems where Mike Holt would be a better choice.
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
I used Soared during my career.
But I think this is an overall electrical theory issue, not simply grounding/bonding, so you should look into transformers/systems where Mike Holt would be a better choice.
I agree I'm lacking the electrical theory
I work for a merit shop so there is no schooling involved but I'm hungry to learn


So would mikes electrical theory course be a good start

Thanks for the reply
 

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
A bit of both

I understanding how a basic wye and Delta transformer work and how the emf from the primary induces a voltage in the secondary

But having a hard time understanding how grounding Influence's the voltages and the effects it has on a system

Plus how its wired in real life in the field

I been doing this for 3 years but I feel like I'm missing something, on the daily I build out large electrical services and I'm the lead mechanic
 

Attachments

  • IMG-20241008-WA0032.jpeg
    IMG-20241008-WA0032.jpeg
    1 MB · Views: 12

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
You could look on you tube also for open delta and corner grounded deltas
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
But having a hard time understanding how grounding Influence's the voltages and the effects it has on a system

Plus how its wired in real life in the field
Read the part of my battery post (no pun intended) where I mentioned grounding one wire. The batteries deliver +1.5v and -1.5v to ground because the center tap is grounded. That's analogous to our 120/240v 1ph system. Two lines with 3.0v between them, and 1.5v to ground.

If the negative end was grounded instead (and the center tap ignored), there would only be +3.0v to ground available. That's analogous to the European 240v 1ph system (which is actually one line from a wye system.)

If you understand what determines line-to-line voltages, then you should get that the voltage to ground from each secondary line depends solely on which other line is (intentionally) grounded. A delta is ground-able in only two ways: One line or the center of one winding.

You may wonder why anyone would want a high-leg service. It may help to understand that the (open) delta began as a 3ph modification to existing 1ph services, where a single piece of 3ph equipment was needed. Thus, the center-tap neutral was pre-existing.

The 208v high-leg voltage is the result of the phase angles between one 240v side of the delta and half of the tapped-secondary's 240v with the 120 degrees thrown in. It's basically mathematics.

Try to give us a better idea of what you're having trouble grasping.
 