Not here hasn’t been available for 20 years
I get utility people opening with statements like that.
I deal with it about 1-2 times a year.
I am confident I could get it one in your area and or any part of the US.
Last edited:
Not here hasn’t been available for 20 years
Not here hasn’t been available for 20 years, but in eastern WA it would be different
I inquired about one in Eastern WA near Spokane, for Inland power. They said they could but overhead only, and overhead obviously has size limitations.I get utility people opening with statements like that.
I deal with it about 1-2 times a year.
I am confident I could get it one in your area and or any part of the US.
You can't get 208 volts from two hots of a high leg delta. The line to line voltage for all combinations is 240 volts.
What do you need the 208 volts for?208 between the high leg and the neutral, thats what I said in my comment
Yeah, they do overhead only because they build it with two different size transformers. Padmounts, if they order them, are limited in unbalanced loads just like the dry types we use. They oversize the center tap transformer, so they don’t have that issue. It’s easy for them to do it that way too, because they are just using two or three 120/240 single phase transformers connected in a delta or open delta configuration. They don’t have to keep an odd transformer that way. Years ago our poco wouldn’t do pad mount 277/480 volt transformers because they had to keep a spare in the yard. They would use pole mounts in a ground enclosure.I inquired about one in Eastern WA near Spokane, for Inland power. They said they could but overhead only, and overhead obviously has size limitations.
Tortuga, I Admire your confidence, but I challenge you to get national grid to provide a high leg delta service.![]()
Im sure it would work just fineThe 208 is for a couple of single phase loads.
My question was about the validity of the high leg to neutral circuit. If someone where to power a load (say 25 Amps/208) from the a high leg panel(the panel is fed from a step down transformer), will the load operate normally? Just like if were connected to 120/208 3 phase where two hot conductors are powering it ?
Sent from my iPhone using Tapatalk
Last year I took a road trip all up and down Northern California, Oregon and Washington, and I saw open delta out in the countryside everywhere just as I figured it might be. In places it would really be hard to replace with wye because of primary configuration.Not here hasn’t been available for 20 years, but in eastern WA it would be different
Just to be clear, I dont think anyone is saying that POCO is making you change to wye, some are just not offering them for new services anymore.Last year I took a road trip all up and down Northern California, Oregon and Washington, and I saw open delta out in the countryside everywhere just as I figured it might be. In places it would really be hard to replace with wye because of primary configuration.
Here in PG&E country it is not going away anytime soon.
What kind of load is it? resisitive ? Inductive?The 208 is for a couple of single phase loads.
My question was about the validity of the high leg to neutral circuit. If someone where to power a load (say 25 Amps/208) from the a high leg panel(the panel is fed from a step down transformer), will the load operate normally? Just like if were connected to 120/208 3 phase where two hot conductors are powering it ?
ITs interesting, Seattle city light says the same thing where they only list "open delta" specifically, with apparently no option for a closed deltaFrom the Dominion Power Blue Book:
120 CHARACTERISTICS OF ELECTRIC SERVICE
120.1 The Company normally provides the following secondary voltages:
• Single-phase: two-wire 120V. (See Section 350 for two-wire 120V line and two-wire 120V
load wiring, and Section 360 for three wire 240/120V line and two-wire 120V load wiring.)
• Single-phase: three-wire 240/120 or 208/120 volts nominal.
• Three-phase: four-wire 208/120 and 480/277 volts grounded wye.
• Three-phase: four-wire 240/120 open delta* volts nominal.
*The service size for this three-phase four-wire 240/120 volt open delta connection shall be
limited to a total of 200 amps per transformer bank. An open delta connection can create
current and voltage unbalances that could potentially damage the Customer’s equipment.
Certain types of equipment, such as motors and refrigeration compressors, are more suscep-
tible to damage with this type of connection. Upgrades of existing delta connections beyond
200 amps are classified as a non-standard voltage connection.
120.2 Requests for secondary voltages not listed above are considered non-standard voltages.
These must have prior approval from the Company’s Planning or Engineering Standards
departments, as well as approval by the Company’s Metering department.
Maybe because if they are going to have three transformers then they are automatically making it a wye service.ITs interesting, Seattle city light says the same thing where they only list "open delta" specifically, with apparently no option for a closed delta![]()
Pacific Graft & Extortion loves it for small 3Ø services.Last year I took a road trip all up and down Northern California, Oregon and Washington, and I saw open delta out in the countryside everywhere just as I figured it might be. In places it would really be hard to replace with wye because of primary configuration.
Here in PG&E country it is not going away anytime soon.