I believe the xfmr is improperly taggd.
'0' is reserved for the neutal-connection where by definition the "neutral conductor" is the one that usually is grounded and has equipotential (excluding phase displacement) measurements from every other conductor. Therefore, although the center-tap of one winding with regard to the two terminals of the same winding of a "red", "high", "bitch", etc-leg delta connection, is technically correct... there is no equipotentil measusurement from all other conductors!
The term "neutral" is used by convention, simply for the lack of a better term. When used in single-phase 3-wire circuits, the term "neutral conductor" is correct.
In 3-phase, 3-wire circuits, there is a "neutral point" that meets the definition above for both the conventional wye and delta-derived systems. In the former, the neutral point is a "physical" one. In the latter, there is no "physical" neutral point, but there is a "virtual' one, namely the centriod of the triangle.
For 4-wire, wye-connected circuits, the "neutral point" is usually "grounded", hence its distribution conductor becomes the "neutral conductor". But, for 4-wire delta-connected circuits like the "grounded-corner" and "mid-point grounded" (both unusual in European practice) the definition is not met. However, by USA convention the "grounded conductor" is labeled the "neutral conductor"! Phew!
Regards, Phil Corso,
Phil, I follow you except the first line. The NP does not have any "0". It has a "GND".