I'm not following this statement.
If we ignore parasitic secondary and primary impedances, but include in our transformer model the primary inductance that creates the magnetic flux in the iron core, my understanding is that the magnetic flux is constant, independent of the load currents. The primary magnetizing current creates the magnetic field in the iron core; that's end of the story when the secondary is open circuit. If we add a secondary load, current flowing in the secondary creates a magnetic flux, which will be precisely canceled by the magnetic flux from the referred current in the primary.
So what's wrong with saying that since the secondary current is equal and opposite in the two half of the split secondary coil, the magnetic fluxes from those two halves will cancel each other, and the referred current in the primary is zero?
The magnetic flux and current are dependent. In a closed delta primary there is always some current flowing so there will be flux in a specific direction, as well as the magnetizing current you mentioned. This is part of the reason many utilities do not like to use 3-legged cores, and instead ask for tri-plex construction which are effectively three single phase transformers in a common metallic tank. Many of these concerns go away with an open delta bank of two separate transformers.