Well, the PV system is not the problem then. There is an additional reactive load added that just happened to be at the same time as the PV system.At this point the inverter is not generating VARs. It is set to power factor of 1
Well, the PV system is not the problem then. There is an additional reactive load added that just happened to be at the same time as the PV system.At this point the inverter is not generating VARs. It is set to power factor of 1
Or a metering error.Well, the PV system is not the problem then. There is an additional reactive load added that just happened to be at the same time as the PV system.
That’s the reason for my post (#20)Or a metering error.
Cheers, Wayne
Yes, the scenario you outlined there is quite plausible, and the pf does get worse, but the meter shouldn't show an increase in kVar for your scenario.That’s the reason for my post (#20)
Possibly it will.Yes, the scenario you outlined there is quite plausible, and the pf does get worse, but the meter shouldn't show an increase in kVar for your scenario.
Cheers, Wayne
I would consider a metering error if this were a standard residential metering setup. Residential meters don't measure VARs since residential customers are generally not billed for peak reactive power usage or low PF as a commercial client might be. But if the existing billing system is billing for VARs then the meter will be tested and certified for measuring VARs. Generally, states are kind of careful that if customers are being billed for something that it is measured by calibrated meters. That being said, it could be that the meter, while being completely accurate at measuring load consumption, is not the correct setup for measuring back feed correctly. Some older meters would read power flow in either direction as usage and bill the customer for exported energy.Or a metering error.
Cheers, Wayne
That being said, it could be that the meter, while being completely accurate at measuring load consumption, is not the correct setup for measuring back feed correctly. Some older meters would read power flow in either direction as usage and bill the customer for exported energy.
Years ago I knew a guy who was doing that, but one month he left the meter flipped too long and the meter reader read a negative usage number. Someone from the utility came out and found where the guy I know had cut the wire right up against the tag and bent it back to make it look uncut. Oops.According to https://forums.mikeholt.com/threads/standard-vs-net-meter.2561707/post-2677754 so called 'secure forward' meters are currently intentionally installed (presumably to prevent people from stealing electricity by reversing the meter).
And my post (#11- get some actual VAR measurements).That’s the reason for my post (#20)