I'm looking at a proposed system that has 480V M-T-M switchgear fed from two separate transformers with each of the transformers being high resistance grounded. I'm familiar with an HRG system on a single transformer/switchgear arrangement but am trying to figure out if there are any special requirements with a M-T-M system.
I would assume that you connect the ground buses between the two Switchgear lineups as you would do on a solidly grounded system however the potential issue I see is that when operating under normal conditions with the tie breaker open the ground bus will be connected to both the HRG's and perhaps cause circulating current? Or will the fault simply follow the least resistant path back to the source transformer through its HRG? Is there any particular considerations here? I'm thinking maybe I'm missing something?
When only one transformer is in operation and being operated through the tie, you will only have one HRG source to which the fault current will return.
I would assume that you connect the ground buses between the two Switchgear lineups as you would do on a solidly grounded system however the potential issue I see is that when operating under normal conditions with the tie breaker open the ground bus will be connected to both the HRG's and perhaps cause circulating current? Or will the fault simply follow the least resistant path back to the source transformer through its HRG? Is there any particular considerations here? I'm thinking maybe I'm missing something?
When only one transformer is in operation and being operated through the tie, you will only have one HRG source to which the fault current will return.