High Resistance Neutral Grounding
High Resistance Neutral Grounding
I have been installing HRNG systems since 1965, so I know a little about them.
In the beginning continuous process facilities like petroleum refineries, that couldn't tolerate outages, used ungrounded systems so that a ground fault would not shut down equipment, which is a catastrophe for them. There are problems with ungrounded system, but they (the refineries) had to live with them. In 1962 Fran Fox (an applications engineer for GE based in San Francisco) came up with the pulser system to locate ground faults in resistance grounded systems. He tested the systems at the Flying A refinery in Martinez, CA, and the Socal refinery in Richmond CA. It was so successful that we converted all 480 volt systems in the Richmond and El Segundo refineries, and later the other Chevron refineries. This system was not acknowledged by the NEC at that time. When the NEC finally acknowledged the HRNG it put some limitations on it, probably out of concern for the skills of "ordinary" electricians. The systems were only to be installed in facilities with trained, on-site electrical staffs who could test them, use the pulser to trace the fault (and then clear the fault at an appropriate time) and understand the system. HRNG avoids system burndowns due to arcing ground faults. For systems rated about 1000 amps the literature was full of burndowns using solidly grounded systems (I have personally seem several of these). The solution was either HRNG or the use of ground fault interrupters (which came into use on low voltage systems in the late 1960s). The HRNG has the advantage of not tripping in the face of the fault. The GFI does trip. Because burndowns almost never happen below 480 volts or in systems with breakers rated below 1000 amps it is not necessary to use HRNG on these systems. I have used HRNG on 2400 and 4160 volts systems, and it works well for these. Above this level they should not be used because the normal leakage current of the system is too high. For systems 4160 volts and below the resisters are sized for approximatley 1 amp (480V) up to 5 amps (2400 and 4160). This level of ground fault can be tolerated for extended periods without damge to the system. Above 4160 the resistor must be set to allow too much fault current so it cannot be used. The fault current must be allowed to exceed the leakage current to maintain system stability, and this is the reason for 1 amp at 480 volts. There are exceptions but by now you are getting MEGO so I won't continue.
The bottom line is simply this: for 240 or 208 volt systems the HRNG offers no advantages. For 480, 2400 or 4180 volts it offers advantages as long as the personnel caring for the system understand it. In 480 volt systems if one wishes to use the neutral for lighting or other loads the HRNG may not be used.
So there you have it. For more info see the IEEE Red Book, the IEEE Green Book, or the IEEE papers published by Fran Fox and Clyde Tipton or Dunke-Jacobs of GE.