- Location
- NYC
- Occupation
- Electrician
I'm working on a high rise in NYC, they have a 500kva generator picking up the whole building.
The feeders from the generator travel from the roof to the basement through the electrical closets(14 floors) to the ATS's
I would consider these emergency feeders (picks up EM lights and elevators)and install a sprinkler head in each closet. I have 2 responses,"everything is emergency so it doesn't matter"
and "the electric rooms are 1 hour rated which satisfies 700.9"
700.9 calls for a 1 hr enclosure dedicated to the emergency circuits.
Should I just comply and move on?
"